I understand I am responsible for monitoring this, I'm not sure where I indicated in my post that I am not?
E-mail alerts are set up, as well as notifications in the web gui both which I check often. Ontop of this, I mainly use the multi_report script for daily e-mail reports on the pool and smart status. (
https://www.truenas.com/community/resources/multi_report-sh-version-for-core-and-scale.179/ https://github.com/JoeSchmuck/Multi-Report/blob/main/multi_report_v2.4.3_2023_06_16.txt)
I am no expert on reading SMART stats. But I am not seeing anything as far as errors go?
So again, my question is based around confusion as to why the spare drives are in use.
I currently do not see the pool showing as degraded or errored. I'm not seeing any smart errors, they all say passed.
And normally I will get a notification from TrueNAS when a drive has an issue, and everytime that has occured, I have replaced the drive. I do not recall seeing the spare drives in use after it is replaced, and re-silvered. And usually when I get a notification that it is having issues, the pool also shows as degraded.
None of these things are currently showing, so I do not understand why spare drives are assigned to those 2 mirrors.
Furthermore, why each mirror has 2 GPTID's showing as spares. I only have 2 spare drives, not 4.
This was the last report the script gave this morning:
Code:
Multi-Report Text Section
External Configuration File in use dtd:2023-06-16
TrueNAS Configuration File --> Emailed every: Mon
Statistical Data File Created.
Statistical Export Log Located: /root/bin/report-generator/statisticalsmartdata.csv --> Emailed every: Mon
WARNING LOG FILE
Drive: N8GEX1NY - Test Age = 405 Days
Drive: N8GEBBRY - Test Age = 405 Days
Drive: NHG9ZP7Y - Test Age = 405 Days
Drive: NHG9JAAY - Test Age = 405 Days
Drive: N8GG3NYY - Test Age = 405 Days
Drive N8GEW7XY High Drive Temp 45 - Threshold set at 45
Drive: N8GEW7XY - Test Age = 405 Days
Drive N8GEX1PY High Drive Temp 45 - Threshold set at 45
Drive: N8GEX1PY - Test Age = 405 Days
Drive: N8GEBDYY - Test Age = 405 Days
Drive: N8GG150Y - Test Age = 405 Days
END
########## ZPool status report for PrimaryPool ##########
pool: PrimaryPool
state: ONLINE
scan: scrub repaired 0B in 14:29:29 with 0 errors on Mon Jul 24 17:29:30 2023
config:
NAME STATE READ WRITE CKSUM
PrimaryPool ONLINE 0 0 0
mirror-0 ONLINE 0 0 0
gptid/d7476d46-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
gptid/d8d6aa36-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
mirror-1 ONLINE 0 0 0
gptid/d9a6f5dc-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
gptid/db71bcb5-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
mirror-2 ONLINE 0 0 0
gptid/d8b2f42f-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
gptid/d96847a9-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
mirror-3 ONLINE 0 0 0
gptid/d9fb7757-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
gptid/da1e1121-32ca-11ec-b815-002590f52cc2 ONLINE 0 0 0
mirror-4 ONLINE 0 0 0
gptid/9fd0872d-8f64-11ec-8462-002590f52cc2 ONLINE 0 0 0
gptid/9ff0f041-8f64-11ec-8462-002590f52cc2 ONLINE 0 0 0
mirror-5 ONLINE 0 0 0
gptid/14811777-1b6d-11ed-8423-ac1f6be66d76 ONLINE 0 0 0
spare-1 ONLINE 0 0 0
gptid/03daa071-505c-11ed-a9fe-ac1f6be66d76 ONLINE 0 0 0
gptid/0d56b97d-1e91-11ed-a6aa-ac1f6be66d76 ONLINE 0 0 0
mirror-6 ONLINE 0 0 0
gptid/749a1891-1b5c-11ee-941f-ac1f6be66d76 ONLINE 0 0 0
spare-1 ONLINE 0 0 0
gptid/4710dd39-1b6d-11ed-8423-ac1f6be66d76 ONLINE 0 0 0
gptid/0d48d4ab-1e91-11ed-a6aa-ac1f6be66d76 ONLINE 0 0 0
spares
gptid/0d48d4ab-1e91-11ed-a6aa-ac1f6be66d76 INUSE currently in use
gptid/0d56b97d-1e91-11ed-a6aa-ac1f6be66d76 INUSE currently in use
errors: No known data errors
Drives for this pool are listed below:
d7476d46-32ca-11ec-b815-002590f52cc2 -> da10
d8d6aa36-32ca-11ec-b815-002590f52cc2 -> da11
d9a6f5dc-32ca-11ec-b815-002590f52cc2 -> da0
db71bcb5-32ca-11ec-b815-002590f52cc2 -> da1
d8b2f42f-32ca-11ec-b815-002590f52cc2 -> da6
d96847a9-32ca-11ec-b815-002590f52cc2 -> da7
d9fb7757-32ca-11ec-b815-002590f52cc2 -> da8
da1e1121-32ca-11ec-b815-002590f52cc2 -> da2
9fd0872d-8f64-11ec-8462-002590f52cc2 -> da4
9ff0f041-8f64-11ec-8462-002590f52cc2 -> da5
14811777-1b6d-11ed-8423-ac1f6be66d76 -> da3
03daa071-505c-11ed-a9fe-ac1f6be66d76 -> da14
0d56b97d-1e91-11ed-a6aa-ac1f6be66d76 -> da13
749a1891-1b5c-11ee-941f-ac1f6be66d76 -> da15
4710dd39-1b6d-11ed-8423-ac1f6be66d76 -> da9
0d48d4ab-1e91-11ed-a6aa-ac1f6be66d76 -> da12
0d48d4ab-1e91-11ed-a6aa-ac1f6be66d76 -> da12
0d56b97d-1e91-11ed-a6aa-ac1f6be66d76 -> da13
########## ZPool status report for boot-pool ##########
pool: boot-pool
state: ONLINE
status: Some supported and requested features are not enabled on the pool.
The pool can still be used, but some features are unavailable.
action: Enable all features using 'zpool upgrade'. Once this is done,
the pool may no longer be accessible by software that does not support
the features. See zpool-features(7) for details.
scan: scrub repaired 0B in 00:01:11 with 0 errors on Sat Jul 29 03:46:12 2023
config:
NAME STATE READ WRITE CKSUM
boot-pool ONLINE 0 0 0
da16p2 ONLINE 0 0 0
errors: No known data errors
########## SMART status report for da0 drive (HGST HUS726040AL4210 : N8GEX1NY) ##########
SMART Health Status: OK
Current Drive Temperature: 42 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48557:09
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 154
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2177
Elements in grown defect list: 1
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 58 0 58 13372934 454302.142 0
write: 0 2828 0 2828 3389882 36543.682 0
verify: 0 0 0 0 410966 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da1 drive (HGST HUS726040AL4210 : N8GEBA2Y) ##########
SMART Health Status: OK
Current Drive Temperature: 44 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48556:03
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 161
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2177
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 55 0 55 12561060 454022.668 0
write: 0 2 0 2 2074132 36441.851 0
verify: 0 0 0 0 515545 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background short Completed - 48542 - [- - -]
########## SMART status report for da2 drive (HGST HUS726040AL4210 : N8GEBBRY) ##########
SMART Health Status: OK
Current Drive Temperature: 43 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48555:50
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 155
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2172
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 33 0 33 13027642 463491.625 0
write: 0 1 0 1 2206321 36533.819 0
verify: 0 0 0 0 393835 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da3 drive (HGST HUS726040AL4210 : NHGAJWEY) ##########
SMART Health Status: OK
Current Drive Temperature: 42 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48287:24
Manufactured in week 06 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 101
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2107
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 24 0 24 14422317 225627.825 0
write: 0 10 0 10 1030410 34952.512 0
verify: 0 0 0 0 630896 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background short Completed - 48273 - [- - -]
########## SMART status report for da4 drive (HGST HUS726040AL4210 : NHG9ZP7Y) ##########
SMART Health Status: OK
Current Drive Temperature: 40 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48339:00
Manufactured in week 06 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 92
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2110
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 13 0 13 13703330 268578.100 0
write: 0 1 0 1 596788 38887.596 0
verify: 0 0 0 0 940657 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da5 drive (HGST HUS726040AL4210 : NHG9JAAY) ##########
SMART Health Status: OK
Current Drive Temperature: 43 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48288:40
Manufactured in week 06 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 96
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2106
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 253 0 253 13668338 256222.301 0
write: 0 10 0 10 2612198 39639.922 0
verify: 0 0 0 0 4764455 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da6 drive (HGST HUS726040AL4210 : N8GG3NYY) ##########
SMART Health Status: OK
Current Drive Temperature: 44 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48556:05
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 150
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2171
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 3 0 3 13486546 468597.936 0
write: 0 0 0 0 1081671 35595.475 0
verify: 0 0 0 0 854699 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da7 drive (HGST HUS726040AL4210 : N8GEW7XY) ##########
SMART Health Status: OK
Current Drive Temperature: 45 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48555:24
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 145
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2161
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 8 0 8 14054491 463057.483 0
write: 0 15 0 15 1651557 35976.650 0
verify: 0 0 0 0 540146 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da8 drive (HGST HUS726040AL4210 : N8GEX1PY) ##########
SMART Health Status: OK
Current Drive Temperature: 45 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48541:30
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 146
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2162
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 66 0 66 12497339 468147.414 0
write: 0 1 0 1 2412800 36459.509 0
verify: 0 0 0 0 523748 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da9 drive (HITACHI HUS72604CLAR4000 : K4K0BBJB) ##########
SMART Health Status: OK
Current Drive Temperature: 42 C
Drive Trip Temperature: 60 C
Accumulated power on time, hours:minutes 37508:38
Manufactured in week 17 of year 2017
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 177
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 1709
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 25 0 25 20915848 413392.882 0
write: 0 7 0 7 674346 107703.687 0
verify: 0 2 0 2 1626590 645.024 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background short Completed - 37494 - [- - -]
########## SMART status report for da10 drive (HGST HUS726040AL4210 : N8GEBDYY) ##########
SMART Health Status: OK
Current Drive Temperature: 39 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48541:05
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 136
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2151
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 165 0 165 13039442 454258.839 0
write: 0 7 0 7 1532709 35740.830 0
verify: 0 0 0 0 527317 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da11 drive (HGST HUS726040AL4210 : N8GG150Y) ##########
SMART Health Status: OK
Current Drive Temperature: 43 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48540:39
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 142
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2160
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 7 0 7 11730523 438780.105 0
write: 0 2 0 2 2201948 35673.478 0
verify: 0 0 0 0 382295 0.000 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background long Self test in progress ... - NOW - [- - -]
########## SMART status report for da12 drive (HITACHI HUS72604CLAR4000 : K4K7KU5B) ##########
SMART Health Status: OK
Current Drive Temperature: 42 C
Drive Trip Temperature: 60 C
Accumulated power on time, hours:minutes 36851:41
Manufactured in week 20 of year 2017
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 240
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 1635
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 1 0 1 10847030 499394.074 0
write: 0 0 0 0 699292 115861.436 0
verify: 0 0 0 0 50685 785.723 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background short Completed - 36838 - [- - -]
########## SMART status report for da13 drive (HITACHI HUS72604CLAR4000 : K4K6EM8B) ##########
SMART Health Status: OK
Current Drive Temperature: 41 C
Drive Trip Temperature: 60 C
Accumulated power on time, hours:minutes 36852:32
Manufactured in week 20 of year 2017
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 236
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 1625
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 1 0 1 10259926 501568.651 0
write: 0 4 0 4 506902 118108.487 0
verify: 0 0 0 0 54679 771.884 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background short Completed - 36838 - [- - -]
########## SMART status report for da14 drive (HITACHI HUS72604CLAR4000 : K4J3EXNB) ##########
SMART Health Status: OK
Current Drive Temperature: 41 C
Drive Trip Temperature: 60 C
Accumulated power on time, hours:minutes 35452:54
Manufactured in week 20 of year 2017
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 198
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 1540
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 2 0 2 11315287 499496.148 0
write: 0 0 0 0 762551 116007.798 0
verify: 0 0 0 0 64344 771.487 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background short Completed - 35439 - [- - -]
########## SMART status report for da15 drive (HITACHI HUS72604CLAR4000 : K3GM0E6L) ##########
SMART Health Status: OK
Current Drive Temperature: 40 C
Drive Trip Temperature: 60 C
Accumulated power on time, hours:minutes 42673:33
Manufactured in week 37 of year 2017
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 9
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 1784
Elements in grown defect list: 0
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 21 0 21 11282273 420332.175 0
write: 0 175 0 175 1471694 445962.959 0
verify: 0 716 0 716 363406 3614.828 0
Non-medium error count: 0
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Background short Completed - 42659 - [- - -]
########## SMART status report for da16 drive (SanDisk SDSSDH3 512G : 21280S800845) ##########
SMART overall-health self-assessment test result: PASSED
ID# ATTRIBUTE_NAME FLAG VALUE WORST THRESH TYPE UPDATED WHEN_FAILED RAW_VALUE
5 Reallocated_Sector_Ct 0x0032 100 100 --- Old_age Always - 0
9 Power_On_Hours 0x0032 100 100 --- Old_age Always - 15142
12 Power_Cycle_Count 0x0032 100 100 --- Old_age Always - 88
165 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 327683
166 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 0
167 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 21
168 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 1
169 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 181
170 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 0
171 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 0
172 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 0
173 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 0
174 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 15
184 End-to-End_Error 0x0032 100 100 --- Old_age Always - 0
187 Reported_Uncorrect 0x0032 100 100 --- Old_age Always - 0
188 Command_Timeout 0x0032 100 100 --- Old_age Always - 0
194 Temperature_Celsius 0x0022 067 040 --- Old_age Always - 33 (Min/Max 11/40)
199 UDMA_CRC_Error_Count 0x0032 100 100 --- Old_age Always - 136
230 Unknown_SSD_Attribute 0x0032 001 001 --- Old_age Always - 0
232 Available_Reservd_Space 0x0033 100 100 004 Pre-fail Always - 100
233 Media_Wearout_Indicator 0x0032 100 100 --- Old_age Always - 11
234 Unknown_Attribute 0x0032 100 100 --- Old_age Always - 33
241 Total_LBAs_Written 0x0030 253 253 --- Old_age Offline - 21
242 Total_LBAs_Read 0x0030 253 253 --- Old_age Offline - 659
244 Unknown_Attribute 0x0032 000 100 --- Old_age Always - 0
No Errors Logged
Num Test_Description (Most recent Short & Extended Tests - Listed by test number)
# 1 Short offline Completed without error 00% 15128 -
# 3 Extended offline Completed without error 00% 15082 -
SCT Error Recovery Control: SCT Commands not supported
End of data section
The only thing I am seeing that stands out is this in the report script.. which is stating these drives have not been tested in 405 days. This makes no sense to me.
WARNING LOG FILE
Drive: N8GEX1NY - Test Age = 405 Days
Drive: N8GEBBRY - Test Age = 405 Days
Drive: NHG9ZP7Y - Test Age = 405 Days
Drive: NHG9JAAY - Test Age = 405 Days
Drive: N8GG3NYY - Test Age = 405 Days
Drive N8GEW7XY High Drive Temp 45 - Threshold set at 45
Drive: N8GEW7XY - Test Age = 405 Days
Drive N8GEX1PY High Drive Temp 45 - Threshold set at 45
Drive: N8GEX1PY - Test Age = 405 Days
Drive: N8GEBDYY - Test Age = 405 Days
Drive: N8GG150Y - Test Age = 405 Days
If I go into TrueNAS's Web GUI > Storage > Disks > N8GEX1NY (da0) > SMART Test Results > I see 20 listings, all say status "Success" and it is currently running a long background test.
Here is the smartctl -a for that drive:
Code:
# smartctl -a /dev/da0
smartctl 7.2 2021-09-14 r5236 [FreeBSD 13.1-RELEASE-p7 amd64] (local build)
Copyright (C) 2002-20, Bruce Allen, Christian Franke, www.smartmontools.org
=== START OF INFORMATION SECTION ===
Vendor: HGST
Product: HUS726040AL4210
Revision: A980
Compliance: SPC-4
User Capacity: 4,000,787,030,016 bytes [4.00 TB]
Logical block size: 512 bytes
Physical block size: 4096 bytes
LU is fully provisioned
Rotation Rate: 7200 rpm
Form Factor: 3.5 inches
Logical Unit id: 0x5000cca244194888
Serial number: N8GEX1NY
Device type: disk
Transport protocol: SAS (SPL-3)
Local Time is: Wed Aug 2 16:04:58 2023 EDT
SMART support is: Available - device has SMART capability.
SMART support is: Enabled
Temperature Warning: Enabled
=== START OF READ SMART DATA SECTION ===
SMART Health Status: OK
Current Drive Temperature: 42 C
Drive Trip Temperature: 85 C
Accumulated power on time, hours:minutes 48557:18
Manufactured in week 29 of year 2016
Specified cycle count over device lifetime: 50000
Accumulated start-stop cycles: 154
Specified load-unload count over device lifetime: 600000
Accumulated load-unload cycles: 2177
Elements in grown defect list: 1
Vendor (Seagate Cache) information
Blocks sent to initiator = 5855174732021760
Error counter log:
Errors Corrected by Total Correction Gigabytes Total
ECC rereads/ errors algorithm processed uncorrected
fast | delayed rewrites corrected invocations [10^9 bytes] errors
read: 0 58 0 58 13372934 454302.142 0
write: 0 2828 0 2828 3389888 36543.693 0
verify: 0 0 0 0 410966 0.000 0
Non-medium error count: 0
SMART Self-test log
Num Test Status segment LifeTime LBA_first_err [SK ASC ASQ]
Description number (hours)
# 1 Background long Self test in progress ... - NOW - [- - -]
# 2 Background short Completed - 38827 - [- - -]
# 3 Background short Completed - 38803 - [- - -]
# 4 Background short Completed - 38779 - [- - -]
# 5 Background short Completed - 38755 - [- - -]
# 6 Background short Completed - 38731 - [- - -]
# 7 Background short Completed - 38707 - [- - -]
# 8 Background short Completed - 38683 - [- - -]
# 9 Background long Completed - 38671 - [- - -]
#10 Background short Completed - 38659 - [- - -]
#11 Background short Completed - 38635 - [- - -]
#12 Background short Completed - 38611 - [- - -]
#13 Background short Completed - 38587 - [- - -]
#14 Background short Completed - 38563 - [- - -]
#15 Background short Completed - 38539 - [- - -]
#16 Background short Completed - 38515 - [- - -]
#17 Background long Completed - 38510 - [- - -]
#18 Background short Completed - 38491 - [- - -]