SOLVED Will this UPS work? APC Back-UPS BE850M2

canute4444

Dabbler
Joined
Jul 7, 2021
Messages
16
I have this APC Back-UPS BE850M2 model connected to my TrueNAS server.
It is showing up as Back-UPS ES 850G2 on the Server
Code:
# dmesg | grep ugen
ugen0.1: <0x8086 XHCI root HUB> at usbus0
ugen0.2: <American Power Conversion Back-UPS ES 850G2 FW:931.a10.D USB FW:a10> a
t usbus0

I tried a few different combinations of Driver, Username and Password. But when I start the service, within a few seconds the service seems stop automatically.
UPS.png

I keep seeing ERR ACCESS-DENIED and forced shutdown in progress in the logs
Code:
# tail -40 /var/log/messages
Nov 14 11:15:15 Cloud 1 2021-11-14T11:15:15.841476-05:00 Cloud.lan upsmon 36639 - - Login on UPS [ups@localhost:3493] failed - got [ERR ACCESS-DENIED]
Nov 14 11:15:20 Cloud 1 2021-11-14T11:15:20.842767-05:00 Cloud.lan upsmon 36639 - - UPS ups@localhost:3493: forced shutdown in progress
Nov 14 11:15:20 Cloud 1 2021-11-14T11:15:20.843152-05:00 Cloud.lan upsmon 36639 - - FSD set on UPS ups@localhost:3493 failed: ERR ACCESS-DENIED
Nov 14 11:15:20 Cloud 1 2021-11-14T11:15:20.843287-05:00 Cloud.lan upsmon 36639 - - Executing automatic power-fail shutdown
Nov 14 11:15:20 Cloud 1 2021-11-14T11:15:20.853090-05:00 Cloud.lan upsmon 36639 - - Auto logout and shutdown proceeding

The UPS information seems accurate too
Code:
# upsc ups
battery.charge: 97
battery.charge.low: 10
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2020/07/08
battery.runtime: 1700
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 13.7
battery.voltage.nominal: 12.0
device.mfr: American Power Conversion
device.model: Back-UPS ES 850G2
device.serial: 4B2028P16913
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ugen0.2
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: APC HID 0.96
driver.version.internal: 0.41
input.sensitivity: medium
input.transfer.high: 139
input.transfer.low: 92
input.transfer.reason: input voltage out of range
input.voltage: 121.0
input.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 931.a10.D
ups.firmware.aux: 10
ups.load: 23
ups.mfr: American Power Conversion
ups.mfr.date: 2020/07/08
ups.model: Back-UPS ES 850G2
ups.productid: 0002
ups.realpower.nominal: 450
ups.serial: 4B2028P16913
ups.status: FSD OL CHRG
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d


What settings should I be using?
 

jdvoracek

Cadet
Joined
Nov 14, 2021
Messages
4
Try Monitor User = upsmon and Monitor Password = fixmepass. My APC uses the same driver, and that seems to be the expected combination, but I don't remember where I got that. Good luck!
 