I'm running FreeNAS 9.3-RELEASE and have an OpenUPS2 as here:
http://www.mini-box.com/OpenUPS2
FreeNAS runs a program called NUT (network ups tools) for the UPS service.
NUT officially only supports the OpenUPS but not the OpenUPS2 (actually recently fixed but hasn't made it to FreeNAS yet)
The solution is very simple.
Place the text "productid=d005" in the "auxiliary parameters" field of the UPS Service settings page in FreeNAS.
I've confirmed that I get notifications (console and email) when the power is unplugged, and when it plugs back in. With the "UPS On Battery" option for shutdown and 30s timer I verified that the UPS service will shut down the system in an orderly fashion after power loss. I occasionally get a COMMBAD alert by email but it seems to be an intermittent polling issue with the driver and has no effect on operation.
If you're having any issue getting it to work, first check is that the USB connection is recognized. If you look in the console there is a boot message like below indicating the UPS is identified by the operating system.
In this case it also means you should select select ugen0.3 in the UPS config page.
If you want to test or debug anything you can open the shell and do the following:
(this assumes you've already tried to start the UPS using the GUI and specified "ups1" as the identifier in the UPS config page, which will setup the config files especially ups.conf)
verify /usr/local/etc/nut/ups.conf exists and has an entry under "ups1".
run upsd to start the UPS service (See the MAN page for details)
run "upsc ups1" to list details about the UPS.
Note some of the values like voltage are whacky, from what I can tell this may be fixed in a future version of NUT but does not affect operation in the mean time.
You may also need to manually start the driver. The driver for OpenUPS2 is "usbhid-ups"
You can run it with the following:
note the productid=d005 is the added config info needed for the OpenUPS2 from the FreeNAS GUI mentioned above.
You may get a bunch of errors when you run this. For me it output a bunch of info about the UPS and then eventually gave a "libusb_get_report: Unknown error". However this does not seem to impact the functioning of the UPS. upsd responds when the power is pulled and plugged back in, will shutdown the system in an orderly fashion, and sends emails just fine.
Anyway, hopefully this is way too much info as all you really need to do is enter the 1 line in the auxiliary parameters box.
freenas kernel: ugen0.3: <Mini-Box.Com> at usbus0 freenas kernel: uhid0: <Mini-Box.Com OPEN-UPS2, class 0/0, rev 2.00/0.03, addr 3> on usbus0
[root@freenas] ~# upsc ups1 battery.capacity: 100 battery.charge: 100 battery.charge.low: 5 battery.charge.warning: 20 battery.current: 0.000 battery.mfr.date: battery.runtime: 3932100 battery.temperature: 28.09 battery.type: battery.voltage: 10.14 device.mfr: Mini-Box.Com device.model: OPEN-UPS2 device.serial: LI-ION device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: /dev/ugen0.3 driver.parameter.productid: d005 driver.version: 2.7.2 driver.version.data: openUPS HID 0.1 driver.version.internal: 0.38 input.current: 0.000 input.voltage: 432.42 output.current: 0.000 output.voltage: 313.20 ups.mfr: Mini-Box.Com ups.model: OPEN-UPS2 ups.productid: d005 ups.serial: LI-ION ups.status: OL ups.vendorid: 04d8 [root@freenas] ~#
/usr/local/libexec/nut/usbhid-ups -u root -x productid=d005 -a ups1