Another update on the installation of the new rack mount ups and a power savings (assumed) comparison. I had hoped to do some measured temperature stats, but I've got to help the Better Half get ready for our grandson's b-day party. There's a mention about heat at the end (yes, you have to read it all) :p:p:p
Measured from a single CyberPower CP1000PFCLCD model which is plugged into a 20amp 120v wall outlet.
With all devices at idle, the UPS is showing readings of (output in watts) = 252
-------------------------------------------------------------------------------------------------------------
Equipment Listed Below:
2 - Dell N2024 switches (stacked)
1U pfSense Firewall/Router Server
X9SCM-F | E3-1230 V2 | 16GB RAM | Server
X11SSM-F | Pentium G4400 | 32GB RAM | Server
--------------------------------------------------------------------------------------------------------------
The same equipment as listed above now runs more efficiantly @240v
with a new HPE R /T3000 G4 HV NA/JP UPS Model J2R02A (Rebadged Eaton 5PX3000IRT2U)
plugged into a 20amp 240v (L-6 20R) wall outlet.
With all the devices at idle, the UPS is showing readings of:
output in watts = 216 | output in VA = 359 | 1.5amps | PowerFactor = 0.60
-------------------------------------------------------------------------------------------------------------
It's obvious the Eaton designed UPS is far more superior at monitoring and listing the measurements of power usage for the unit compared to the CyberPower unit. The price difference indicates it should be this way.
I could have been far more detailed in the measurement part of this comparison, but I have to many irons in the fire at this point and can spare no more time for this.
In conclusion, I would also like to point out that all the heat that exits the rear of these machines has been reduced by a noticeable amount. To be blunt, the air coming out now, feels much cooler than it did when everything was running off of 120v power. I am very happy with the less than $320 investment (I also spent some money on fancy power cables), with the power savings AND heat reduction, the hardware purchased will pay for itself in no time.