The UI for NUT allows one to set a timer in upssched.conf in order to shutdown Freenas (but inexplicably not the UPS, see bug 4134) a fixed time after the UPS goes on battery. The time setting for this timer is in a box which is greyed out when waiting for a low battery condition to shutdown Freenas, the default use case that does not use upssched.conf for deciding when to shutdown.
'FINALDELAY' is a setting in upsmon.conf which governs, following a another delay of default 15sec to allow slave systems to communicate, how long upsmon waits after deciding a shutdown is inevitable before actually shutting down Freenas. This perhaps explains the observation some in the forum have commented on that if the on battery delay is set to several minutes then NUT waits another several minutes before implementing its decision to shutdown. The default value of FINALDELAY is, I think, 5 seconds, and it should be very short as by default it follows a warning that the UPS battery is running out. Actually there seems no point at all in FINALDELAY but that is a decision of the NUT team!
Even worse, if one changes one's mind and uses the GUI to request a shutdown on low battery rather than a certain time after going on battery, then the inappropriate value of FINALDELAY is left behind and there is no way through the GUI to alter it.
This unexpected and unwanted delay in shutting down when the UPS battery is known to be about to fail is clearly dangerous to the filesystem!
Can anyone think of a reason why this may be intended behaviour before I report this as a serious bug (and ask for 4134 to be fixed at the same time as it is so trivial and safe to fix)?
Edited for sentence order only, in order to make sense, 31/8/14
Roger
'FINALDELAY' is a setting in upsmon.conf which governs, following a another delay of default 15sec to allow slave systems to communicate, how long upsmon waits after deciding a shutdown is inevitable before actually shutting down Freenas. This perhaps explains the observation some in the forum have commented on that if the on battery delay is set to several minutes then NUT waits another several minutes before implementing its decision to shutdown. The default value of FINALDELAY is, I think, 5 seconds, and it should be very short as by default it follows a warning that the UPS battery is running out. Actually there seems no point at all in FINALDELAY but that is a decision of the NUT team!
Even worse, if one changes one's mind and uses the GUI to request a shutdown on low battery rather than a certain time after going on battery, then the inappropriate value of FINALDELAY is left behind and there is no way through the GUI to alter it.
This unexpected and unwanted delay in shutting down when the UPS battery is known to be about to fail is clearly dangerous to the filesystem!
Can anyone think of a reason why this may be intended behaviour before I report this as a serious bug (and ask for 4134 to be fixed at the same time as it is so trivial and safe to fix)?
Edited for sentence order only, in order to make sense, 31/8/14
Roger