NUT slaves. How do I configure the Low Battery value?

DarkCorner

Explorer
Joined
Oct 23, 2022
Messages
66
I have TrueNAS SCALE configured with NUT Slave.
If I set the value Shutdown Mode = "UPS reaches low battery" where do I set the value "low battery?
The "Shutdown Timer" field states in the description "...This value only applies when Shutdown mode is set to UPS goes on battery"
 

MisterE2002

Patron
Joined
Sep 5, 2015
Messages
211
i used (on CORE)

Auxiliary Parameters (ups.conf)
Code:

# https://networkupstools.org/docs/man/usbhid-ups.html

desc = "APC SMT750I"

ignorelb

lowbatt = 86
 

DarkCorner

Explorer
Joined
Oct 23, 2022
Messages
66
It didn't work, maybe because mine is Slave?
But I understand that a line must be inserted in the NUT configurations.
 

MisterE2002

Patron
Joined
Sep 5, 2015
Messages
211
to be sure. the mentioned snippit you add to "Auxiliary Parameters (ups.conf)", this is a input field (in CORE at least).

Also useful "upsc -L" and "upsc" to verify the connection them.
 